Power is supplied to the Flex System Enterprise
Chassis when one end of each power cord is connected to a power
connector on the rear of the chassis and the other end of each power
cord is connected to a power distribution unit (PDU) or uninterruptible
power source (UPS).
Connecting for N+N power redundancy
The Flex System Enterprise
Chassis can have up to six power supplies. The chassis allows
you to populate power supplies to meet the load demand that is installed
in the chassis. As more nodes are installed in the chassis, you can
install additional power supplies to meet the increased load demand.
Attention: If there is not enough power available from
the power supplies to meet the load demand installed in the chassis,
the Chassis Management Module will not allow some of the devices to power on.
To provide power source redundancy for the chassis, you can connect
the power supplies in an N+N configuration, where N can be 1, 2 ,
or 3, depending on the total load installed in the chassis. In this
configuration, the power-supply power cords are connected to separate
PDUs. If a supply circuit fails, the remaining power supplies have
enough power available to power the entire chassis load. A fully configured
chassis with N+N power redundancy has six power supplies.
Connecting for N+1 power redundancy
If power source redundancy is not a concern but you want power supply
redundancy, you can connect the power supplies in an N+1 configuration,
where N can be 1, 2, 3, 4, or 5 depending on the total load that is
installed in the chassis. In this configuration, the power-supply
power cords are connected to the same PDU but there is one extra power
supply available (+1). If one of the power supplies fails, the remaining
power supplies have enough power available to power the entire chassis
load. If two or more power supplies fail, it is possible for the entire
chassis to lose power. If the power source circuit fails, the entire
chassis will lose power.
Statement 29
CAUTION:
This equipment is designed to permit the connection
of the earthed conductor of the dc supply circuit to the earthing
conductor at the equipment. If this connection is made, all of the
following conditions must be met:
- This equipment shall be connected directly to the dc supply system
earthing electrode conductor or to a bonding jumper from an earthing
terminal bar or bus to which the dc supply system earthing electrode
conductor is connected.
- This equipment shall be located in the same immediate area (such
as, adjacent cabinets) as any other equipment that has a connection
between the earthed conductor of the same dc supply circuit and the
earthing conductor, and also the point of earthing of the dc system.
The dc system shall not be earthed elsewhere.
- The dc supply source shall be located within the same premises
as this equipment.
- Switching or disconnecting devices shall not be in the earthed
circuit conductor between the dc source and the point of connection
of the earthing electrode conductor.
Statement 31
DANGER
Electrical
current from power, telephone, and communication cables is hazardous.
To avoid a shock hazard:
- Do not connect or disconnect any cables or perform installation,
maintenance, or reconfiguration of this product during an electrical
storm.
- Connect all power cords to a properly wired and grounded power
source.
- Connect to properly wired power sources any equipment that will
be attached to this product.
- When possible, use one hand only to connect or disconnect signal
cables.
- Never turn on any equipment when there is evidence of fire, water,
or structural damage.
- Disconnect the attached ac power cords, dc power sources, network
connections, telecommunications systems, and serial cables before
you open the device covers, unless you are instructed otherwise in
the installation and configuration procedures.
- Connect and disconnect cables as described in the following table
when you install, move, or open covers on this product or attached
devices.
To Connect: |
To Disconnect: |
- Turn OFF all power sources and equipment that is to be attached
to this product.
- Attach signal cables to the product.
- Attach power cords to the product.
- For ac systems, use appliance inlets.
- For dc systems, ensure correct polarity of -48 V dc connections:
RTN is + and -48 V dc is -. Earth ground should use a two-hole lug
for safety.
- Attach signal cables to other devices.
- Connect power cords to their sources.
- Turn ON all the power sources.
|
- Turn OFF all power sources and equipment that is to be attached
to this product.
- For ac systems, remove all power cords from the chassis power
receptacles or interrupt power at the ac power distribution unit.
- For dc systems, disconnect dc power sources at the breaker panel
or by turning off the power source. Then, remove the dc cables.
- Remove the signal cables from the connectors.
- Remove all cables from the devices.
|
Statement 34
CAUTION:
To
reduce the risk of electric shock or energy hazards:
- This equipment must be installed by trained service personnel
in a restricted-access location, as defined by the NEC and IEC 60950-1,
First Edition, The Standard for Safety of Information Technology Equipment.
- Connect the equipment to a properly grounded safety extra low
voltage (SELV) source. A SELV source is a secondary circuit that
is designed so that normal and single fault conditions do not cause
the voltages to exceed a safe level (60 V direct current).
- Incorporate a readily available approved and rated disconnect
device in the field wiring.
- See the specifications in the product documentation for the required
circuit-breaker rating for branch circuit overcurrent protection.
- Use copper wire conductors only. See the specifications in the
product documentation for the required wire size.
- See the specifications in the product documentation for the required
torque values for the wiring-terminal screws.
Attention: The following circuit breaker and ground cable
ratings apply to -48 V dc power supplies only:
Breaker |
Listed 70 A |
See Note 1 |
Ground cable |
4 AWG with Listed lug which can accept M6 ground
screws |
See Note 2 |
Torque rating for ground screws |
4.0 - 4.8 Newton-meters (35.4 - 42.5 inch-pounds) |
- |
- The maximum steady state current of the -48 V dc power supply
is less then 70 A. However during specific events, such as over subscription,
it is possible for the power supply to briefly draw a current greater
than 70 A. Therefore it is recommended that the power supply be protected
by a Listed circuit breaker that will support up to 90 A for a minimum
of 20 ms. The suggested Telect High Current Panel Dual 350A Power
Distribution Panel (part number 350CB06) using the Telect 70 A circuit
breakers (Part number 090-0052-0070) conforms to this specification.
- If not connecting to a SELV source which provides Reinforced insulation
you must use a Ground Cable.
|
To connect the chassis to power, complete the following steps:
- For an ac-powered chassis (restricted-access location
is not required), connect each power cord from the power supplies
to a power distribution unit (PDU), uninterruptible power source (UPS)
or wall receptacle. AC power is supplied to the Flex System Enterprise
Chassis by one of the following options:
- A power cord that connects to a PDU or UPS supplying a maximum
20 A branch circuit protection.
- A power cord that connects to a wall receptacle supplying a maximum
20 A branch circuit protection.
- A special use Flex System 3X
Power Cord that connects to a wall receptacle supplying a maximum
32 A branch circuit protection.
Attention: Do not route the power cords over removable
modules or allow the cords to interfere with the module handles.
- For dc-powered chassis:
- For a chassis powered by -48 to -60 V dc power supplies
(restricted access location is required), connect an earth
ground cable to each power supply.
- Use a 10 mm nut driver to remove the hex nuts from the ground
studs.
- Remove the lock washer and one of the flat washers from each ground
stud.
- Push the ground lug onto the ground studs; then, place the flat
washer, the lock washer, and the hex nut back on each ground stud.
- Use a 10 mm nut driver to tighten the hex nuts to 4.0 - 4.8 Newton-meters
(35.4 - 42.5 inch-pounds).
- Connect each power cord from the dc power supplies to a dc power
distribution unit (PDU) (restricted-access location is not required).
Attention:
- Do not route the power cords over removable modules or allow the
cords to interfere with the module handles.
- In North America, connect the power cords to a UL-listed PDU only.
- Make sure that the following LEDs are lit:
- The logo on the chassis front information panel.
- The dc power and ac power LEDs on each power supply.
- The power LED on each I/O module.
Note: The power LED on each compute node and
on the Flex System Manager management node, if one is installed, flashes slowly to indicate
that the node is connected to power and is ready to be turned on.
- If the LEDs are not lit:
- Disconnect the chassis from the power source.
- Reseat all of the components in the chassis.
- Reconnect the chassis to the power source.
- If the problem persists, contact Support.