An Over-Temperature Condition has been detected on [ProcessorElementName].
Explanation
The temperature of microprocessor 2 has exceeded the critical level,
causing a hard shutdown of the compute node.
May also be shown as
806f01070302ffff or 0x806f01070302ffff
Severity
Error
Alert Category
Critical - Temperature
Serviceable
Yes
CIM Information
Prefix: PLAT and ID:
0036
SNMP Trap ID
0
Automatically notify Support
No
User response
Complete the following steps until the problem is solved:
- Check the Chassis Management Module or Flex System Manager event log
for any fan- or cooling-related issues.
- Make sure that the airflow at the front and rear of the chassis is not
obstructed and that fillers are in place and correctly installed.
- Make sure that the room temperature is within operating specifications.
- Make sure that the microprocessor heat sink is securely installed.
- Make sure that the microprocessor heat sink is installed correctly and
the thermal material is correctly applied.
- Replace microprocessor 2.