Before connecting cables or powering the Flex System Carrier-Grade
chassis,
you must connect the chassis to earth ground.
Statement 29
CAUTION:
This
equipment is designed to permit the connection of the earthed conductor
of the dc supply circuit to the earthing conductor at the equipment.
If this connection is made, all of the following conditions must be
met:
- This equipment shall be connected directly to the dc supply system
earthing electrode conductor or to a bonding jumper from an earthing
terminal bar or bus to which the dc supply system earthing electrode
conductor is connected.
- This equipment shall be located in the same immediate area (such
as, adjacent cabinets) as any other equipment that has a connection
between the earthed conductor of the same dc supply circuit and the
earthing conductor, and also the point of earthing of the dc system.
The dc system shall not be earthed elsewhere.
- The dc supply source shall be located within the same premises
as this equipment.
- Switching or disconnecting devices shall not be in the earthed
circuit conductor between the dc source and the point of connection
of the earthing electrode conductor.
Statement 34
CAUTION:
To reduce the risk of electric shock
or energy hazards:
- This equipment must be installed by trained service personnel
in a restricted-access location, as defined by the NEC and IEC 60950-1,
First Edition, The Standard for Safety of Information Technology Equipment.
- Connect the equipment to a properly grounded safety extra low
voltage (SELV) source. A SELV source is a secondary circuit that is
designed so that normal and single fault conditions do not cause the
voltages to exceed a safe level (60 V direct current).
- Incorporate a readily available approved and rated disconnect
device in the field wiring.
- See the specifications in the product documentation for the required
circuit-breaker rating for branch circuit overcurrent protection.
- Use copper wire conductors only. See the specifications in the
product documentation for the required wire size.
- See the specifications in the product documentation for the required
torque values for the wiring-terminal screws.
Attention: The following circuit breaker and
ground cable ratings apply to chassis equipped with -48 V dc power
supplies:
Breaker |
Listed 70 A |
See Note 1 |
Ground cable |
4 AWG with Listed lug which can accept M6 ground
screws |
See Note 2 |
Torque rating for ground screws |
4.0 - 4.8 Newton-meters (35.4 - 42.5 inch-pounds) |
- |
- The maximum steady state current of the -48 V dc power supply
is less then 70 A. However during specific events, such as over subscription,
it is possible for the power supply to briefly draw a current greater
than 70 A. Therefore it is recommended that the power supply be protected
by a Listed circuit breaker that will support up to 90 A for a minimum
of 20 ms. The suggested Telect High Current Panel Dual 350A Power
Distribution Panel (part number 350CB06) using the Telect 70 A circuit
breakers (Part number 090-0052-0070) conforms to this specification.
- If not connecting to a SELV source which provides Reinforced insulation
you must use a Ground Cable.
|
To connect the chassis to earth ground, complete the following
steps:
- Connect an earth ground cable to the ground studs on the rear
of the chassis:
- Use a 10 mm nut driver to remove the hex nuts from the ground
studs.
- Remove the lock washer and one of the flat washers from each ground
stud.
- Push the ground lug onto the ground studs; then, place the flat
washer, the lock washer, and the hex nut back on each ground stud.
- Use a 10 mm nut driver to tighten the hex nuts to 4.0 - 4.8 Newton-meters
(35.4 - 42.5 inch-pounds).